Secondary cables are susceptible to lightning surge currents when substation is struck by lightning. Little work has been made to the effects of surge currents in substation secondary cables, particularly the effects of surge current rise time. Six types of simulated lightning surge currents with different rise times, ranging from 5.7 μs to 25.4 μs, were injected into the substation grounding grid, and the inductive voltage from core wire to ground and the shield current in the closed loop of the buried secondary cable were measured simultaneously. The inductive coupling characteristics and the effect of rise time on shielding factor (SF) of buried secondary cables were investigated using time-frequency domain method. The results indicate that the surge current with shorter rise time will induce higher core-wire voltage and higher the shield current on the secondary cable. Double-end grounding of the shielding layer can significantly reduce the cable coupling response, especially reduce the high-frequency component of the inductive voltage at 10 to 100 kHz with steeper surge currents. The SF of secondary cable increases exponentially from 1.91 dB to 8.15 dB as the rise time of the lightning surge current decreases.