Dissolved gas analysis (DGA)in power transformers is related to the degradation of insulation materials and dissolved methane (CH 4 )is a symbol gas of low energy electrical or thermal faults in power transformer oil. Conventional online DGA equipment suffers from problems such as cross sensitivity, electromagnetic compatibility and reliability. Based on tunable diode laser absorption spectroscopy (TDLAS) technique, a novel optical method is proposed to detect dissolved methane in transformer oil. Oil samples with fault gases are prepared and dissolved methane detection has been carried out in the laboratory. 1653.72 nm is selected as the central wavelength of tunable diode laser, moreover, a multipass gas cell and wavelength modulation strategy is utilized to trace methane dissolved in oil. Results show that the resolution of detection reaches 0.28 µL/L, and accuracy is less than 2 µL/L at low concentration. In addition, the detection cycle is so time-saving, less than 5 minutes. The proposed measurement method shows tremendous advantages, such as immediate response to concentration changes, no cross interference, no carrier gases, which is proved to be a promising maintain-free technique instead of conventional DGA equipment.