AbstractOne crucial objective of this article is to present simplified and accurate approaches to study the current distribution and ground surface potential around the area surrounding an earthed and isolated system in case of a line‐to‐earth fault. The present study is done in the case of uniform and two‐layer soils. Suggested models for calculating the distribution of the earth's surface current density, step, and touch voltages in grounded and isolated systems are presented, discussed, and adapted. The contact and arc resistances of line to ground faulty conductors are considered. Rods and/or grounding grids usually do grounded systems. The impact of both step and touch potentials and current density are investigated in this article. The methods of the calculations are based on the electrical concepts, the charge simulation method, and the imaging procedure for the grounding system. The suggested method can be considered a novel and simple technique for calculating the current distributions of the ground surface during line to ground fault. The results agree with those obtained by others, with the advantage of the proposed algorithm for its ease of application and simplicity. 3‐D dimensions’ contours of the current density and the electric potential on the earth surface around the faulty point are presented in case of homogeneous and two layers’ soil. Finally, this article's novelty is to devise a method for calculating the step and touch potentials and current density around the point of contact of the conductor carrying the electric voltages in the event of faults occurring in the electrical network, whether the network is grounded or isolated. Such faults of electrical networks may cause human hazards.