The maximum ceiling height of the FM Global laboratory is 18.3 m. Therefore, fire protection solutions for warehouses with taller ceilings cannot be directly validated through full-scale testing. This work develops a methodology to obtain the key processes of fire growth, spray-plume interaction, and fire suppression response for an 18.9 m high roll-paper storage under a 24.4 m tall ceiling. The proposed methodology uses a heptane burner assembly at the base of the commodity array to match the fire heat release and growth rate to that of a taller storage exceeding lab capability. The burner assembly included six heptane burners and two air ducts. A series of experiments was conducted to characterize the burner design, model the fire growth in the free-burn stage, and validate controlled and uncontrolled fires in terms of the number of activated sprinklers. A final large-scale fire test used a 12.8 m high storage of Kraft paper with the burner assembly under an 18.3 m tall ceiling to validate protection recommendations for Kraft paper stored 18.9 m high under a 24.4 m tall ceiling. The test demonstrated full suppression using K360 (K-factor, lpm/bar1/2), fast response, pendent sprinklers with a temperature rating of 74 °C, supplied with a water pressure of 8.3 bar.