This research focuses on studying the flexural behaviour of reinforced concrete beams externally strengthened with bonded CFRP laminates and subjected to high temperature (fire) for different exposure time and two cooling schemes (air and water). 12 reinforced concrete beams with 1,000 mm loading span and cross-sectional area of 100 × 200 mm and reinforced with 2 bars 12 mm diameter as main reinforcement were tested. The CFRP used was laminates of 50 mm width and 1.2 mm thick which were protected from fire using a perlite mortar cover of thickness 5 cm. The beams were loaded to their working load, and while maintaining the load, they were subjected to fire for 1, 2 and 3 h, respectively, then followed by cooling either by water or by left to slow cool in air at room temperature. After cooling, the load was increased up to failure. The structural behaviour of the tested beams was studied by applying a three-point bending test and the mid-span deflection was recorded using LVDT. The mode of failure was investigated and presented. Also, a comparison between strengthened and unstrengthened beams was performed and presented. The results show that the fire protective layer is essential to maintain and minimize the loss in the strength gained by applying CFRP laminates. Also, it indicates that abrupt water cooling reduces the strength gained by about 15–29%.