This study presents a new strategy for column base plate connections, which involves the utilization of welded anchor rods positioned concentrically beneath the base plate, in alignment with the connected column. The objective was to remove the eccentricity between the anchor rods and the column, thereby excluding the base plate from the load-transferring chain. A numerical study was performed to compare the cyclic behavior and uplift response of the proposed connection with conventional column base connections. Additionally, different weld types were investigated to connect the anchor rods to the base plate, and their efficiency was evaluated based on a comprehensive dataset of nine tests on equivalent base-plate T-stub connections with different base-plate thicknesses, anchor-rod strengths, and anchor-rod diameters. The numerical results showed that using welded anchor rods could remove the pinching from the hysteresis loops, as the anchor rods can effectively resist cyclic loads in both compression and tension. Furthermore, removing the eccentricity between the anchor rods and the column enhanced the uplift stiffness by approximately 31 %. The experimental results indicated that the failure mode was the fracture of anchor rods for all specimens, while the other components remained elastic. The specimens with high-strength anchor rods showed a brittle failure accompanied by a sudden drop in load, which coincided with the fracture of anchor rod in the softened heat-affected zone. All developed weld types successfully withstood the ultimate tensile strength of anchor rods upon fracturing.