The main goal of this research was to evaluate if the existing power supply, which is three-phase, four-wire, and 400 volts, was safe and cost-effective. The study also intends to perform an Electrical System Analysis of the existing 400V, 3-phase, 4-wire power supply, including short circuit calculations, protective device coordination and protection, and arc-flash analysis. This research is based on the Philippine Standard of Electrical Design as it is applied and used by electrical professionals in the Philippines. Electrical System Analysis calculations are based on the National Electrical Code, IEEE Standards, and the most recent edition of the Philippine Electrical Code (PEC 2017). According to the findings, the URSM Science and Technology Building's current power supply is adequate and ready for future expansion. It was also cost-effective, as they discovered that the URSM's old ISR Building needed to be upgraded. The Short Circuit Analysis reveals that the installed protective devices' KAIC ratings are underrated and should be upgraded. The protective device coordination and protection reveals that the protective equipment must have a 0.2 to 1 second time setting. The required PPE for the building's electrical maintenance staff is shown in the arc flash analysis. This study's overall implications provide necessary inputs and corrective measures for the safety of URSM faculty, students, and other stakeholders.