This study explores the optimization of wavy-slit fins in the indoor units of air conditioners that use low-global-warming-potential refrigerants, with a focus on the interactions between slit length, width, and height. A response surface method was employed to analyze the trade-offs between thermal performance and pressure loss, and numerical optimization was performed using two objective functions: pumping power and volume goodness factor (Gv). The results demonstrated that optimizing the slits’ geometry significantly enhanced overall performance. For pumping power, a minimum point was observed near the design boundaries, which underscores the critical role of geometric interactions. The flow and temperature field analysis under fixed heat-duty conditions revealed substantial flow separation caused by the slits, enhanced mixing between the upper and lower surfaces, and a reduction of up to 2.05% in pumping power. In contrast, the Gv optimization model exhibited a more uniform flow, reducing flow separation beyond the pipe and improving the Gv by 1.85%, although it led to an increase in pumping power. These findings highlight the potential that tailored slit fin designs have to achieve a balanced enhancement in heat transfer and aerodynamic performance, offering valuable insights for the development of efficient, low-environmental-impact air conditioning systems.