AbstractThe most common disadvantages of loss of excitation (LOE) impedance relay are its improper operation in the conditions of power system disturbances (PSD) and its long operation time. In this regard, to solve the mentioned problems and as a result improve the accuracy and speed of detecting the LOE events, four key variables including active power (Psg), reactive power (Qsg), load angle (δsg), and terminal voltage (Vsg) are selected, on the basis of an in‐depth theoretical‐ and simulation studies. These variables have been implemented in a precise combinational logic. In the developed LOE detection logic of this paper, the dependent parameters of Vsg and Qsg as well as Psg and δsg parameters are examined simultaneously in an AND logic cluster. If both the defined combinations detect the occurrence of LOE, the generator trip command is issued. Otherwise, the normal operation of the under‐study machine will continue. The results of the performed simulations in MATLAB/Simulink environment (2017b) during the detailed scenarios of LOE and PSD events on the IEEE 39‐bus standard system confirm the efficiency of the outlined LOE protection model. Meanwhile, its superiority from the viewpoints of accuracy, swiftness, and simplicity and cost of implementation are comprehensively compared with the other schemes.