Building airtightness significantly impacts its energy use estimation. The fan pressurization test, outlined in ISO 9972, is the most commonly used assessment method. A crucial component is the zero-flow pressure difference, influenced only by wind and stack effects. The ISO 9972 mandates that the absolute value of this pressure difference be less than 5 Pa and the minimum pressure station be either 10 Pa or five times the zero-flow pressure difference. The rationale behind these constraints is not evident, often excluding high-rise and buildings in wind-prone areas from standardized testing.This research examines these ISO 9972 requirements, aiming to clarify their basis and propose alternatives. Equations were developed to connect airflow estimation error with the ratio of the measured pressure station to zero-flow pressure difference. The external pressure measurement location during the test was found pivotal in determining airflow errors due to ISO constraints. While existing constraints limit airflow errors in many scenarios, enhancements are possible. If ISO 9972 conditions are unfeasible, always maintaining a 10 Pa buffer across façades can contain maximum airflow errors. This study suggests an alternative constraint with a similar error range (about 15 %) to current ones, enabling standardized testing in environments where existing ISO conditions are unattainable.
Read full abstract