Various advanced control sequences for chiller plants with water-side economizers (WSE) have been proposed in literature, but the evaluation and optimization of those controls is limited. It is possible to maximize energy savings by selecting different sequences and related parameters based on the plant configuration, load, and climate. This paper addresses this gap by developing near-optimal advanced control sequences for chiller plants with WSEs. First, advanced control sequences for chiller plants with WSEs are categorized into condenser water, chilled water, and hybrid controls and representative sequences from each category are identified. Next, 504 different scenarios are optimized. These scenarios represent all possible combinations of two plant configurations, a constant or variable load profile, three advanced control sequences, and seven optimization parameter combinations in six climate zones. The results show the recommended near-optimal sequences can reduce energy consumption by up to 15% relative to the baseline depending on the configuration, load profile, and climate. Specifically, the CW-CHW sequence is recommended for the majority of systems because it is often the most energy efficient and/or reduces the runtime of chillers. The methodology in this paper provides practical guidance for achieving energy savings through near-optimal control of chiller plants with WSEs.