AbstractThe receiving‐end system AC fault of the line‐commutated‐converter‐based high voltage direct current (LCC‐HVDC) will lead to commutation failure of the inverter side. During the fault and its recovery, AC transient low voltage and transient overvoltage (TOV) will occur in the sending‐end system. The TOV has the risk of triggering the disorderly off‐grid of the nearby renewable power generations. Besides, in a serious situation, it will threaten the power system to maintain a secure and steady operation. Therefore, the authors analyse the mechanism involved in the AC transient voltage during the AC fault and the recovery period first. It reveals that the key factor causing the TOV of the sending‐end system is the setting of the DC current reference value. Then, a DC current reference value limit method based on the AC TOV sampling value is proposed, which is used to accelerate DC current recovery and suppress the TOV of the sending‐end system. Finally, the effectiveness of the designed control method has been confirmed through electromagnetic transient simulations using the CIGRE HVDC benchmark model and a ±800 kV HVDC transmission system model situated in Northwest China.