Metrological characterisation of static energy meters under realistic low power quality conditions is a basic requirement for proper grid control and fair energy billing. The paper reports about a new proposed methodology, where the meters are tested under conditions directly recorded at installation sites. The waveforms of voltages and currents are sampled using a portable instrument; they are reproduced in laboratory conditions with a phantom power generator, with a bandwidth covering up to the 40th harmonic. The recording site is a photovoltaic energy production facility, having a a nominal power of 50 kW, at the coupling section to the grid. These waveforms were then reproduced in the laboratory, and tested on different models of single- and three-phase commercial static energy meters; the models chosen represent both energy meters used by energy providers at the point of common-coupling, and also meters typically used for in-line monitoring by end users. The quantity of interest is the reading error of the measured energy, when tested with the conditions reproduced from the on-field measurements, in comparison with a reference meter. All tested energy meter models comply with the present international documentary standards, which require tests under low power quality conditions; nevertheless, there are models that show unacceptable errors (up to 25%) in the measurement of active energy when tested with the on-field recorded waveforms. This suggests that the standardised testing waveforms might, in some cases, be not fully representative of the actual conditions encountered in the field.