Decentralised, wall mounted ventilation is one of alternative to typical – cross flow or “heat wheel” recovery air handling units (AHU) system when it is not possible to install it. It solves problems such as the need for more space, power consumption of fans, and investment costs. This experimental study aims to analyse the performance of the unique constructed decentralised air handling unit (DAHU) prototype that has a special balls-packed regenerative heat exchanger. The development of the DAHU also aimed to simplify the operation and production of the unit to make it more affordable and easier to manufacture. As the DAHU is constructed from individually sized components, the pressure losses of the diffuser, the regenerator, the screens to hold the balls, the filter and the fan were measured and the actual DAHU airflow was determined. The general operation of the DAHU was tested in a climatic chamber to determine the appropriate cycle times for this type of device, as well as the heat recovery efficiency at different outdoor air temperatures. Five different DAHU operating cycles were analysed. It was found that the duration of supply air must be longer than the duration of extract air to achieve higher efficiency. Therefore, DAHU's subsequent heat exchanger studies were performed for four airflows. The highest DAHU heat recovery efficiency was achieved (above 70%) with a supply and extract duration of 150 s. It has been found that the efficiency of this DAHU increases with decreasing outdoor air temperature because of the storage properties of the balls. The analysis showed that this type of DAHU could be suitable for use in cooler and colder climates.