Roof fans have gradually replaced the non-powered hood as supplementary power to increase exhaust rate in high-rise residential kitchen shafts. However, an effective control strategy for roof fans is lacking. This paper studies the constant static pressure strategy and deduces its control parameters based on required exhaust rate and non-distributed data transmission. First, the static pressure set value (SV) is investigated under the worst exhaust condition, considering variations in shaft heights and measuring positions (MP). Then, an on/off mechanism is set up based on the measured static pressure and the fan frequency when the exhaust rate is adequate. Results show that under the recommended shaft sizes and design concurrent usage rates, the SVs for users' exhaust rate reaching 500 m³/h are −60, −60, and 0 Pa for 10/18/26-floor shafts when the MP is at a shaft's outlet, and roof fans are turned on when the static pressure reaches 100, 90, and 90 Pa and turned off when the fan frequency is below 32, 30, and 22 Hz. The MP at the shafts' outlet can keep the shaft at a slightly negative pressure. Control parameters for specific applications can be obtained through the proposed calculation process. An 18-floor shaft study found that the constant static pressure strategy can achieve 50 % energy savings compared to the constant frequency operation of the roof fan. These findings contribute to reliable control without users' distributed data transmission and to lower energy consumption of the residential kitchen exhaust system.