In high-voltage transmission lines, secondary arcs severely affect the stability of power systems. However, there has been no research to combine transmission line model with time-varying resistance secondary arc. In this study, the improved arc dynamics model, the Mayr resistance model, and the transmission line system were combined in the simulation model to investigate the influence of the compensation reactor, line length, and short-circuit fault location on the characteristics of secondary arc current. The results revealed that the inhibitory effect of shunt reactors was the best at the midpoint between the fault point and the end of transmission line. When the series reactance satisfied a certain value, the short-circuit current was considerably suppressed with only a slight increase in the secondary current. The lower resistance along the line and longer transmission lines accelerated the secondary arc extinction rapidly. The location of the short-circuit fault had a limited effect on secondary arc extinction. The arc extinction time fluctuated within a small range with the changes in the location of the short-circuit fault. The results of the study can provide a reference for suppressing secondary arc currents.