Turn-to-turn short circuit faults in the primary winding of generator terminal voltage transformers can lead to erroneous operation of stator grounding protection systems. This paper analyzes the fault characteristics associated with such failures and derives formulas for the fault phase current and zero-sequence voltage during a turn-to-turn short circuit in the primary winding. A 3D finite element model of the generator terminal voltage transformer is established by using Altair Flux 3D, and the accuracy of the model is verified. Based on this model, simulation tests were conducted to investigate turn-to-turn short circuits in the primary winding. The results reveal that as the number of shorted turns increases, the voltage of the fault phase decreases continuously while the voltages of the other two phases increase. The current in the short-circuited phase rises significantly, accompanied by an increase in zero-sequence voltage. Visualizations of magnetic field parameters indicate that as the number of shorted turns increases, the magnetic induction magnitude of the fault phase rises steadily and approaches saturation, resulting in heightened magnetic field intensity near the shorted turns. This analysis of fault characteristics through simulation contributes to the advancement of fault diagnosis systems for generator terminal voltage transformers.