As the power consumption of electronic components continues to rise, liquid cooling technology has become the mainstream solution for cooling electronic devices. This study designs a double-layer serpentine microchannel cold plate with a ribbed structure and firstly investigates the effects of the flow path on thermal–hydraulic performance of the cold plate. Through orthogonal numerical tests, the impact of rib height, number of rib truncations, rib truncation gap, and rib end deviation distance on thermal–hydraulic performance of cold plate is analyzed, along with their significance. Based on the results of the orthogonal test, the optimal rib structure parameters are determined. Results show that the parallel flow path has a more uniform flow distribution and approximately 2.5 % lower thermal resistance of the cold plate than the series flow path. Higher rib height leads to a higher convective heat transfer coefficient, more uniform internal flow distribution, and lower thermal resistance. When the rib height increases from 0.3 mm to 3 mm, the convective heat transfer coefficient increases 18 %, and the thermal resistance of the cold plate decreases 12 %. Compared to the initial structure, the optimized structure at the highest PEC has total thermal resistance and pressure drop reduced by 5.5 % and 7.4 %, respectively, while the structure with the lowest thermal resistance has a 7.9 % reduction in thermal resistance but a 27 % increase in pressure drop.