A lightning current measurement method using a Rogowski coil based on an integral circuit with low-frequency attenuation feedback was proposed to address the issue of low-frequency distortion in the measurement of lightning currents on transmission lines using Rogowski coils. Firstly, the causes of low-frequency distortion in lightning current measurements using Rogowski coils were analyzed from the perspective of frequency domains. On this basis, an integration correction optimization circuit with a low-frequency attenuation feedback network was designed to correct the low-frequency distortion. The optimized integration circuit can also reduce the impact of low-frequency noise and the DC bias of the operational amplifier (op-amp) on the integration circuit due to the high low-frequency gain. Additionally, a high-pass filtering and voltage-divided sampling circuit has been added to ensure the normal operation of the integrator and improve the measurement range of the measurement system. Then, according to the relationship between the amplitude-frequency characteristics of the measurement system and the parameters of each component, the appropriate types of components and op-amp were selected to expand the measurement bandwidth. Finally, a simulation verification was conducted, and the simulation results show that this measurement method can effectively expand the lower measurement frequency limit to 20 Hz, correct the low-frequency distortion caused by Rogowski coils measuring lightning currents on transmission lines, and accurately restore the measured lightning current waveform.