In recent years, the frequency of forced oscillation events due to control system malfunctions or improper parameter settings has increased. Tuning the parameters of exciters and governor models is crucial for maintaining power system stability. Traditional simulation studies typically involve small transient disturbances or step changes to find optimal parameter sets, but existing optimization algorithms often fall short in fine-tuning for forced oscillations. Identifying the sensitive parameters within these control models is essential for ensuring stability during large, sustained disturbances. This study focuses on identifying these critical exciter and governor model parameters by analyzing their influence on sustained forced oscillations. Using Kundur’s two-area system, we analyze common exciter models such as SCRX, ESST1A, and AC7B, along with governor models like GAST, HYGOV, and GGOV1, utilizing PSS®E software version 34. Sustained forced oscillations are injected at generator-1 of area-1, with individual parameter changes dynamically simulated. By considering a local oscillation frequency of 1.4 Hz and an inter-area oscillation mode of 0.25 Hz, we analyze the impact of each parameter change on the magnitude and frequency of forced oscillations as well as on active and reactive power outputs. This novel approach highlights the most influential parameters of each tested model—such as exciter, governor, and turbine gains, as well as time constant parameters—on the impact of forced oscillations. Based on our findings, the sensitive parameters of each tested model are ranked. These would provide valuable insights for industry operators to fine-tune control settings during oscillation events, ultimately enhancing system stability.