Abstract The medium voltage switchgear is a key equipment in the distribution network of the power system, which directly faces users. Once a fault occurs, it will cause huge economic losses and adverse social impacts. Partial discharge measurement is an important means to ensure the safe operation of switchgear. The physical quantities measured by different partial discharge detection methods are different, so the detection effects by different methods for the same defect are also different. This paper takes the common internal air gap defects of solid insulation in switchgear as the research object, and conducts partial discharge detection tests on real switchgear equipment. At the same time, radio frequency method, ultrasonic method, transient earth voltage (TEV) method, and pulse current method are used to detect and analyze the partial discharge generated by the defect. The results show that the radio frequency method, TEV method, and pulse current method have good detection sensitivity for air gap defects, but the ultrasonic method cannot detect this type of defect. Comparing the amplitudes of the three electrical signals, it can be found that the correlation between the TEV method and the pulse current method is relatively high, while the correlation between the radio frequency method and the two is relatively low. As the applied voltage increases, the amplitude of the radio frequency method changes linearly, which can more sensitively reflect the degree of defect change.