Faulty synchronizations of synchronous generators can cause significant detrimental effects, primarily due to a large current and high electromagnetic torque. These effects not only impact the generator but they can also extend to the prime mover and the step-up transformer. Furthermore, such events can trigger disturbances in the power system, potentially leading to system collapse if not promptly cleared. Although the autosynchronizers and synchro-check technologies are well established in the industry, faulty synchronizations, such as those caused by incorrect wiring during maintenance or commissioning operations, can go undetected by these systems. Existing protections do not allow for the detection of faulty synchronizations in a timely manner. This paper presents novel protection methods specifically designed for this issue: one based on instantaneous current value and the other on the instantaneous current-derivative value. These schemes are activated exclusively during the synchronizations process, allowing for faster fault detection compared to existing methods, thereby reducing the duration of harmful electrical and mechanical stresses after a faulty synchronization. The effectiveness of the proposed schemes has been validated through computer simulations of a 362 MVA turbo-generator from a thermal power plant and also through experimental tests on a 5 kVA synchronous generator using a specialized laboratory synchronization test bench, yielding promising results.