The polarization and depolarization current (PDC) measurement has been widely used to assess the aging degree of cross-linked polyethylene (XLPE) cables. However, the aging type identification of XLPE cables has not been fully considered. In this study we conduct PDC measurement on thermal-aged and water tree-aged XLPE cable samples respectively, upon which a graphical approach to assess the insulation condition and distinguish the aging type of XLPE cables is proposed. First, to designate the evaluation indexes of the insulation condition, multiple PDC measurement based dielectric parameters are considered. Then, to reflect the sensitivity of each evaluation index to the condition of XLPE cable, a combined weighting method based on the group fuzzy analytic hierarchy process (GFAHP) and entropy method (EM) is introduced. Furthermore, the improved radar chart method (RCM) based graphical approach is proposed to comprehensively and intuitively characterize the evaluation indexes. Finally, the aging degree of the XLPE cable samples is quantitatively assessed by calculating the area of the polygon in the chart. Simultaneously, utilizing the position of the areal coordinate and the shape characteristic parameter of the polygon, the thermal-aged and water tree-aged samples are effectively distinguished.