For the LCL -type grid-connected inverter, grid voltage full feedforward scheme is an effective method to improve the quality of the injected grid current. However, in the applications where a step-up transformer is adopted and its leakage inductance serves as the grid-side inductor, it is difficult to directly measure the grid voltage. For this case, the capacitor voltage full feedback scheme is proposed in this article to suppress the injected grid current distortion due to the grid voltage harmonics, and the full feedback function includes proportional, derivative, and second-derivative components. It is found that the derivative component counteracts the capacitor current feedback active damping, and both of them can be removed. Thus, the current sensor for sensing the capacitor current is saved. Instead, the LCL filter resonance is damped by the proportional and second-derivative feedback components, and a low-pass filter is added to the second-derivative component for ensuring a positive equivalent resistance within the full controllable frequency range. Experimental results from a 6-kW single-phase grid-connected inverter are provided to verify the effectiveness of the proposed method.