Low Voltage Ride Through (LVRT) is considered one of the main and serious problems facing the electrical grid. It occurs due to three-phase symmetric faults and asymmetric faults such as a double line to ground fault that applies in this system. This paper applies Static Synchronous Compensators (STATCOM) to improve the LVRT capability and dynamic performance of an electrical grid linked to a Photovoltaic (PV)/Wind hybrid system through grid disturbances. A hybrid power system containing a PV station that produces 1 MW and a wind farm from type Doubly Fed Induction Generator (DFIG) that produces 9 MW is connected to STATCOM with 48 pulses at PCC bus and energized load. It compensates reactive power to improve LVRT that occurred due to fault. The applied STATCOM controller adjusts the voltage of the PCC bus during an occuring fault on the grid by compensating reactive power. STATCOM is controlled by a Proportional–Integral–Derivative (PID) and is compared with STATCOM controlled by Artificial Intelligence Control (AIC)-based on Proportional—Integral Fuzzy Logic Control (PI FLC). The Lightning Attachment Procedure Optimization Algorithm (LAPO) optimization method is used to adjust the parameters of the PI controller to reduce error signals. A simulation model of the suggested hybrid power system has been performed using Matlab/Simulink. The simulation results of STATCOM proved powerful and the effectiveness of STATCOM with PI FLC in reducing voltage dip, compensating active power of wind and PV farm, protecting DC-link voltage of PV and wind from overvoltage and oscillation that happens at three-phase fault and double line to ground fault as compared with PID STATCOM in enhancement LVRT capability, and power quality.