To analyze the influence of environmental parameters on cold-end systems, especially the natural draft wet cooling tower (NDWCT), and the thermal system, the 660 MW power plant was taken as the research subject. Based on Ebsilon, this paper researched numerically the cooling performance of NDWCT and thermal system under different environmental conditions. The simulation results showed that increasing dry bulb temperature and environmental humidity causes a decline of water temperature drop (△t), which deteriorates the cooling performance and leads to adverse effects on the thermal system. As dry bulb temperature rises from 20℃ to 30℃, total power generation and system efficiency drop by 6484.89 kW and 0.18 %, respectively, and drop by 9912.72 kW and 0.86 % when environmental humidity elevates from 35 % to 75 %. Meanwhile, simulation investigations demonstrated that crosswind affects seriously NDWCT and further affects the thermal system. When crosswind speed increases from 0.21 m/s to 4.75 m/s, △t and system efficiency drop by 1.6℃ and 0.17 %, respectively, and gross coal consumption rate rises by 1.14 g/(kW∙h), which leads to the reduction of thermal system economy. In all, influence of environmental parameters on cold-end system, especially NDWCT, and the entire thermal system were revealed, which provided a basis for dynamic analysis of coal-fired power plants.