BACKGROUND: Carbon dioxide can be an alternative refrigerant for vapor compression refrigeration systems, particularly air conditioning systems (ACSs). However, its use suffers from the increased pressure in the refrigeration circuit. To solve this, for its reduction, a mixture of CO2 with a substance that has significantly lower pressures under the same conditions can be developed, for example, dimethyl ether (DME), which has zero GWP and ODP, is inexpensive and readily available. The study of DME, in particular, was conducted by the Department E4 “Refrigeration and Cryogenic Engineering, Air Conditioning and Life Support Systems” of N.E. Bauman Moscow State Technical University. DME is moderately toxic and flammable.
 AIM: This study aims to investigate the possible use of a mixture of DME and carbon dioxide for energy-efficient application in ACSs using commercially available compressors for R410A.
 METHODS: Comparative calculation analysis of the characteristics of a simple one-stage vapor compression cycle was performed using R410A and a mixture of DME and CO2 using the calculation packages Mathcad 15, Aspen HYSYS v. 10, SOLKANE8, and REFPROP.
 RESULTS: 1. The cycle on pure DME is the most effective in terms of the coefficient of performance: ε = 5.63 at an ambient air temperature of 26°C, ε = 3.07 at 40°C. 2. It is necessary to consider the influence of temperature glides, the average value of which ranges from 10°C to 30°C depending on the concentration of components. 3. At DME/CO2 ratios of 40/60% and 60/40% (in mole fraction), the discharge pressure corresponds to the discharge pressure in the R410A cycle, with 39.62 bar at an ambient temperature of 26°C and 37 bar at 40°C, respectively.
 CONCLUSIONS: An environmentally friendly mixture of DME and CO2 with low GWP and zero ODP is developed. An increase in the percentage of DME in the mixture increases the coefficient of performance and reduces the pressure range, and at the same time, significant temperature glides arise, which affects the installation efficiency, namely, the transition to a cycle with a receiver tank, i.e., with a recuperative heat exchanger between the fluorinated refrigerant flow leaving the evaporator and the fluorinated refrigerant flow leaving the condenser. The developed mixture is less efficient than the R410A refrigerant in terms of the coefficient of performance and discharge pressure. However, it is possible to further consider a mixture of DME and CO2 with concentrations of 40% and 60%, respectively, as a replacement for the R410 refrigerant because there is a correspondence of discharge pressures for serial compressors (about 40 bar); however, it is necessary to keep in mind the flammability risk of the mixture.