The indoor DC yard of the ±1100 kV UHVDC transmission project is preferred to the outdoor solution, and the rational design of shielding electrodes for the ±1100 kV apparatus becomes the key to system security. In this paper, the design requirements of indoor DC yards were described and the preliminary designs of the indoor shielding electrodes for the key ±1100 kV DC apparatus were proposed. The whole 3-D FEM model of one ±1100 kV indoor DC yard was established. An empirical formula of the critical E-field strength for the evaluation of relatively large shielding electrodes was proposed based on the corona tests of typical ball and ring electrodes. The electric field distribution of the whole indoor DC yard was calculated and the surface electric field strength of all the shielding electrodes for the key ±1100 kV apparatus was evaluated. The results show that after optimization, the maximum surface field strength on the shielding electrode of ±1100 kV DC filter capacitor decreased from 1507 V/mm to 1335 V/mm, lower than the critical value for evaluation, then the corona free design of all the ±1100 kV indoor shielding electrode could be predicted. The method of electric field evaluation and optimization could provide important references for the development of shielding electrodes in the ±1100 kV or other UHV indoor DC yards.