Abstract Due to the inability of the grid-type control method to compensate for the comprehensive reduction in system inertia, strength, and short-circuit capacity caused by the proportional decrease of synchronous machines, the power grid exhibits insufficient resistance to disturbances, leading to severe stability risks in terms of rotor angle, frequency, and voltage. In response to these challenges, grid-forming inverters have emerged. Under symmetrical faults, the low-voltage ride-through of grid-forming inverters is often accompanied by a frozen reactive power environment, resulting in a direct output of increased voltage and reactive current. However, an elevated reactive power command can cause a sharp increase in the potential amplitude within grid-forming inverters. After the grid fault is cleared, the excessively high internal potential can cause a short-term and rapid increase in terminal voltage, potentially leading to overvoltage, which is detrimental to the operation of grid-connected devices. To address this issue, this paper first employs a grid-forming inverter controlled by a virtual synchronous machine control method. Using the grid positive-sequence voltage as a reference value, it identifies whether a voltage drop fault has occurred. Based on this, an adaptive reactive power control strategy is proposed, which can promptly achieve the same effect as the frozen reactive power environment during faults, while also promptly restoring the reactive power environment after fault clearance, thereby avoiding overvoltage issues. The feasibility of the proposed method is verified through the establishment of a simulation system.