This article shows the local boiling HTCs of R134a and three low-GWP replacements, R1234yf, R1234ze(E) and R152a within a (BPHE). The experimentation was performed in a test-section specially set up for the measurement of the local two-phase HTC at a saturation temperature of 10 °C, with a refrigerant mass velocity from 9.5 to 35.2 kg m−2 s−1, incoming vapour quality between 0.2 and 0.3 and almost complete vaporisation. Both nucleate boiling and forced-convection boiling play an important role in these tests, depending, mainly, on the location along the plate. The comparison with theoretical models shows that both Longo et al. (2015) and Amalfi et al. (2016) models reproduce very well the experimental HTCs. The measurement of local temperature profiles within the BPHE allows to couple the evaluation of thermal and hydraulic performances of refrigerants into a single parameter named Total Temperature Penalty (TTP). The TTP analysis highlights similar boiling performance for R134a, R1234yf and R152a refrigerants, while R1234ze(E) displays worse performance.