Aim: The access of the medium-voltage (MV) microgrid changes the radial structure of traditional distribution networks, causing the distribution network to operate in a closed-loop manner. The closed-loop operation complicates the fault characteristics of the distribution network, and the traditional single-phase grounding (SPG) line selection method is no longer applicable. Therefore, it is necessary to propose a new targeted SPG line selection method. Methods: This paper analyzes the network structure of MV microgrids and MV distribution networks and establishes a multi-level closed-loop operation distribution network model with MV microgrid access. Then, the SPG fault characteristics of the closed-loop operation distribution system under the small current grounding mode are analyzed from the perspective of two-level bus nodes. Furthermore, based on the analysis of fault characteristics, a closed-loop operation distribution network line selection method suitable for microgrid access is proposed, and a detailed design is carried out in terms of equipment configuration and communication schemes, forming a relatively complete automatic line selection system. At the same time, the proposed line selection scheme is based on the two-level bus nodes, which can be analogously applied to the multi-level closed-loop operation distribution network. Results: The simulation results show that the proposed line selection scheme can be effectively applied to the closed-loop operation distribution network with MV microgrid access. Conclusion: The traditional SPG line selection method will have misjudgment problems after the MV microgrid is integrated into the distribution network, but the line selection method proposed in this paper has good adaptability.