The building envelope can afford many enhancements for lowering the cooling load in hot regions. In this paper, an active upgraded model utilizing an evaporative system to cool the envelope will be tested in the relatively humid climate of the coastal area of the Arabian Gulf. A couple of buildings were erected for this purpose. One was fully enclosed by a secondary structure around it, and the gap between the two was cooled using an evaporative cooler. This was compared to the second, which was insulated according to Dubai Municipality standards. A third comparison was also performed, which concerned the standalone secondary envelope with no evaporative cooling. The interior of all three cases was cooled using DX window-type air conditioners, and the power consumption measured. Thermal simulations were performed on similarly designed models using Ecotect 5.5 to see how each system would perform in full-scale functioning buildings. The measured tests on the building models showed a reduction of electrical consumption in both upgrades compared to the regulation insulated reference. The secondary envelope provided savings of 40 % and 47.3 % in the hot months of June and July, while the evaporative solution saved 52.1 % and 53.7 %, respectively. The simulation of a full-size building over the entire year showed the secondary envelope saving 48.9 % and the evaporative assisted 57.15 %.