In order to investigate the seismic performance of earthquake-damaged high-strength recycled aggregate concrete (HSRAC) beam-column interior joints employing ultra-high strength bars (UHSB) in columns, four specimens were designed and manufactured. The research variables included whether the steel tube was encased in the column and whether beams were rehabilitated by bonding steel plates. Among them, the rehabilitated specimens were firstly loaded to 1.0 % drift ratio, and then loaded to failure after rehabilitating the plastic hinge of beams. The test results showed that the beam hinge failure mode occurred in the specimens loaded directly to failure. The damage of columns and joint cores was relatively slight, and the crack width satisfied the repairability limits before 2.0 % drift ratio. The shear failure of the joint core occurred in the rehabilitated specimen without steel tube, as shear deformation and stirrup strain in the joint core increased. The shear bearing capacity of joints increased after steel tubes were encased in columns, and the damage of joint cores was reduced. The bearing capacity and deformation capacity of specimens improved after rehabilitating. Finite element models were established and verified with experiment results. Parameter analysis was conducted for different pre-damage degrees, and the results indicated that as pre-damage degree increased, the bearing capacity of specimens decreased.