Locating fault precisely on power transmission line is highly beneficial to utilities and accurate fault location can expedite the repair of the faulted components, speed-up restoration, and reduce outage time. In this paper, a setting-free double ended fault location method for power transmission line is proposed using both end voltage and current measurements. This algorithm estimates the required setting parameters using pre-fault data and fault location is calculated using estimated parameters and during fault data. The proposed method is verified using the EMTDC simulations for lines connected with conventional and inverter-based renewable resources. The method is not affected by the error in line parameters and renewable integration. The method is implemented in Intelligent Electronic Device (IED) using 1kHz sampling rate and successfully installed on a 400 kV, 233.07 km line from Power Grid Corporation of India (POWERGRID), India and on a 220 kV, 265.6 km line from Svenska Kraftnat (SVK), Sweden. This paper presents laboratory test results as well as field experimental results in which line patrolling crews found the actual location. Pilot installation results match the performance demonstrated with laboratory experimental results. The method gives average fault location error of ~ 0.1 %. The method can locate the fault within two-tower span distance (~300m) which is comparable with traveling wave-based method that requires 1000 times higher sampling rate, high-cost hardware, more complex commissioning, and settings. These geographically diverse pilot installation results stand as testimony to the fault location accuracy of the proposed setting-free fault location solution.