Abstract

Heat collection plates (HCP) are installed above sprinkler heads in some tall halls in the Asia-Oceania region to give faster thermal actuation. In this study, experiments were thus conducted in a fire chamber to determine thermal activation times of sprinkler heads with and without HCP. Three HCP with different diameters were selected and tested with pendent fast response liquid-in-bulb sprinkler heads. A total of 48 sprinklers heads were studied under different conditions of height and pool fire size. The HCP was found to reduce sprinkler activation time in a fire chamber test by up to 61%. Thermal activation time of sprinkler heads was also investigated by the common plunge test in a wind tunnel. Results indicate that activation was delayed by 5%, 18%, and 221% on average by the three HCP. An HCP of pie plate shape with small diameter would alter the physical scenario of heating up the heat sensing element of sprinkler heads assumed in the plunge test. Therefore, the effect of HCP cannot be appropriately assessed in a wind tunnel.

Talk to us

Join us for a 30 min session where you can share your feedback and ask us any queries you have

Schedule a call

Disclaimer: All third-party content on this website/platform is and will remain the property of their respective owners and is provided on "as is" basis without any warranties, express or implied. Use of third-party content does not indicate any affiliation, sponsorship with or endorsement by them. Any references to third-party content is to identify the corresponding services and shall be considered fair use under The CopyrightLaw.