This study evaluates the energy performance of ASHRAE Guideline 36–compliant control (ASHRAE 36 control) and reinforcement learning (RL)–based control through experimental field tests and a simulation study. Three field tests were conducted at Oak Ridge National Laboratory’s commercial building test facility in Oak Ridge, Tennessee: a baseline with a baseline conventional control, a test with ASHRAE 36 control, and a test with RL-based control. The selected ASHRAE 36 controls were trim and respond control, as well as variable air volume (VAV) box control. We compared the measured supply air temperature of the rooftop unit, VAV box supply air temperature, and VAV box supply airflow rate across the three test cases. The field data indicated that ASHRAE 36 controls operated as specified by ASHRAE Guideline 36. Based on these data, ASHRAE 36 control achieved a 45 % reduction in hourly averaged HVAC energy consumption compared with the baseline, and RL-based control achieved a 66 % reduction. These potential annual energy savings were confirmed using a calibrated whole-building energy model. Compared with the baseline, ASHRAE 36 control reduced HVAC energy consumption by 42 %, and RL-based control achieved a 54 % reduction. Furthermore, RL-based control reduced total HVAC energy consumption by 21 % more than ASHRAE 36 control.