In recent years, water-side free cooling has been broadly applied in data centers to lessen the high cost of energy consumption. The energy-saving opportunities of free cooling have been recognized by numerous studies across the world. In this paper, the field test and energy performance evaluation were performed in an operational data center with water-side free cooling, located in Chongqing, China. Existing problems were found during tests, including the insufficient cooling capacity of towers in wintertime and the inability to activate partial-free cooling. The results of the tests show that the reduction in Power Usage Effectiveness (PUE) is much lower than the expected. To understand the marked discrepancies, the performance of the cooling tower was discussed in terms of the approach temperature and actual cooling capacity. The maximum cooling capacity in winter is only about 50% of the rated. With the consideration of the cooling tower configuration performance in different climate conditions, the conservative energy effects were calculated in 34 provincial cities of China. To prolong the hours available, optimized operation schemes of cooling towers are presented. The available hours for free cooling could be increased from 730h to 1300h when operating at 67% of rated flow rate, resulting in a decrease in the energy saving of chillers between 8.44% and 21.05%.