The direct sound transmission through a simple, massive, homogeneous building element with and without lining is investigated experimentally and compared with analytical and empirical models from the literature. A 150 mm thick concrete floor and a 100 mm thick floating floor were measured in the floor transmission facility of the National Research Council Canada, i.e. without flanking sound transmission. In addition to the sound reduction index and the normalized impact sound pressure level, loss factors, radiation efficiencies, and mean squared velocities were recorded in the laboratory. The measured data is compared to established models of sound transmission. A focus is placed on the calculation model of ISO 12354-1 (Appendix B), which uses calculated radiation efficiencies and loss factors to predict the sound reduction index of heavy, homogeneous building elements. Some difficulties with the calculation model and the examples in the standard are discussed. In principle, the results in this study show that the calculation model of ISO 12354-1 gives good estimates when the correct input parameters are used. However, deviations between the calculated and the measured loss factors and radiation efficiencies have large effects on the accuracy of the estimates, particularly in the region around the coincidence frequency.
Read full abstract