Earth–air heat exchangers (EAHX) use the soil thermal capacity to dampen the amplitude of outdoor air temperature oscillations. This effect can be used in hot and dry climates for room cooling, and depending on the EAHX design, this cooling can be achieved with very few resources other than those used during EAHX construction. This is an obvious advantage compared to the significant energy consumption and operational costs of refrigeration machines traditionally used in room cooling. Despite the large number of papers on EAHXs available in the scientific literature, very few deal with large-diameter EAHXs (with pipe diameters larger than 0.30 m), and even fewer present monitoring data gathered from a built and functional large-diameter EAHX. The present paper uses monitoring data and provides a detailed quantitative analysis of the performance of a large-diameter EAHX built for standalone cooling of an existing office building. The field monitoring was carried out during a characteristic hot and dry summer period of the south of Portugal. Results show that outdoor air to EAHX exit air temperature gradients reach 9 K and cooling capacities exceed 27 kW. Moreover, the studied EAHX is capable of standalone cooling for outdoor air temperatures up to 33 °C and meets more than 50% of the room design cooling demand for outdoor air temperatures as high as 37 °C. This evidences that large-diameter EAHXs have the potential to achieve significant reductions in CO2 emissions and in energy consumption associated with building cooling in hot and dry climates.