The non-linearly deterministic fault current characteristics with low current magnitude of high impedance fault (HIF) have thrown an inevitable challenge to the microgrid protection system. Moreover, differentiating HIF from non-fault events is also a challenging task under different operating scenarios of the microgrid. In order to address this, a simple and fast protection algorithm, based on Empirical Mode Decomposition (EMD) in conjugation with Teager-Kaiser Energy Operator (TKEO) is proposed in this article. This scheme process the current signals retrieved from both ends of the line through EMD, and subsequently, the current signal energy is extracted by TKEO. The incidence of a fault is affirmed by measuring the energy difference signal and estimation of entropy. By employing the second layer algorithm using entropy analysis, the non-fault disturbances, such as capacitor and load switching, temporary overloading, and DG outage, have been effectively distinguished from HIFs. The proposed technique is tested for grid-tied and autonomous microgrid operation modes with several HIF and non-fault cases. It is inferred that the proposed technique can detect and differentiate HIFs from other system perturbations seamlessly in less time. Compared to other methods, this scheme has procured excellent accuracy and reliability, and is also not affected by the dynamic current behavior of the microgrid. The PSCAD-EMTDC software is used to build and simulate the test system, and the MATLAB programming interface is utilized to develop and test the suggested method.