In this work we report condensation heat transfer coefficient and pressure drop data for R-454B, R-32, and R-454C. These refrigerants are low Global Warming Potential (GWP) replacements for R-410A. We obtained these data in a smooth 7.2 mm outer diameter (5.94 mm inner diameter) aluminum tube. In these experiments, the key variables were condensation temperature (35 °C ≤Tcond≤50 °C) and refrigerant mass flux (151.1≤G≤347.3 kg m−2 s−1). In general, for similar nominal operating conditions, we measured the highest heat transfer coefficients for R-32 and the lowest for R-454C. Among the correlations we used to predict the heat transfer data for all three refrigerants, the one developed by Thome et al. (2003) predicted the data with the greatest accuracy. Deviations between experimental data and predictions of this correlation were 21.7% for R-454B (with SBG correction), 22.0% for R-32, and 18.8% for R-454C (with SBG correction). Experimental pressure gradient data were predicted by the Friedel correlation Friedel (1979) with deviations of 13.8% for R-454B, 9.8% for R-32, and 10.2% for R-454C. In this work, we also compare the predictions of the Cavallini et al. correlation Cavallini et al. (2006) for R-454B and R-32 in smooth copper versus smooth aluminum tubes. To improve this correlation’s predictive capability for aluminum tubes, we have proposed some modifications. After incorporating these modifications, the deviations between the correlation’s predictions and our data were 10% for R-454B (with SBG correction), 8.1% for R-32, and 5.2% for R-454C (with SBG correction). These data and findings will assist the HVAC and refrigeration industry to implement low-GWP refrigerants in condensers using smooth aluminum tubes.